Dear Mr Ashu Patel There, indeed, had been a lot of argument on the subject of effectiveness of Fusion Bonded Epoxy Coated Bars to prevent corrosion of steel reinforcement embedded in concrete. I quite agree that this can confuse someone who is not very deeply involved in this subject. I, therefore, avail myself of this opportunity to put down a few INCONTROVERTIBLE points on this subject which can be easily appreciated by all concerned.
1. Epoxy coating functions purely as a PASSIVE barrier coating with no ability to provide sacrificial anodic protection. Integrity of the coating is, therefore, an absolute precondition for its ability to prevent corrosion. In real life, however, there are always small gaps in the coating which are commonly called holidays. It has been found that corrosion progresses in a highly localized manner around these holidays. The ruling specification, ASTM A-775 suggests special care during loading, unloading, cutting, bending, straightening in the field, laying etc. which can rupture the coating and therefore, introduce opportunities of local corrosion. However, it is extremely difficult to ensure that adequate precaution is actually taken all through the handling including during pouring and ramming of concrete. Therefore integrity of coating is always a suspect.
2. Epoxy coating is also known to peel off or DISBOND from the base steel during service, making room for severe under-the-film corrosion. To quote from the conclusions of the report to Florida DOT, "
In his report entitled "CORROSION OF EPOXY COATED REBAR IN FLORIDA BRIDGES" (Final Report to Florida D.O.T., WPI No. 0510603, State Job No. 99700-7556-010) Mr Alberio A. Sagues, P.I., Department of Civil I Engineering and Mechanics College of Engineering, University of South Florida observes:
"The present field and laboratory investigation has identified two factors that appear to be critical to the development of severe corrosion in ECR. The first factor is the presence of breaks in the coating that expose some of the metal surface to direct contact with the surrounding electrolyte. Coating breaks relevant to corrosion initiation can range from holidays invisible to the naked eye, produced at the time of manufacturing, to narrow cracks in the coating produced during fabrication bending of tl1e rebar, to macroscopic abrasion, gashes and cuts caused during transportation, field handling and vibration while concreting. The second factor is the development of extensive loss of adhesion between the coating and the base metal after relatively short service times in concrete, even in the absence of chloride ion contamination..........(p-40).. "The most important finding of ECR deterioration in this study was the observation of coating-metal disbondment at almost all of the structures examined. As indicated in the previous section, coating disbondment is considered to be a key step in the corrosion development. The ECR in all these structures appears therefore to be already susceptible to the development of severe crevice corrosion if the chloride concentration reaches the value for corrosion initiation.......(p-4" 这135页的详尽的的全文,高度revealing and impartial research report is available in the following URL:
http://www.cobrae.org/htmlfolder/papers/epoxyrebartestsflorida.pdf
3. Bare steel bars participate in chemical reaction with cement concrete and therefore, there is a formation of a composite layer, which ensures good bond with the concrete. Epoxy coating, being itself nearly neutral to the environment within concrete, precludes formation of any such composite layer. As a result, there is a perceptible drop in the bond strength of epoxy coated bars when compared with uncoated deformed bars.
There are a few more finer points given below which are also worth noting:
a. Study has also shown that chloride irons are able to permeate even the undamaged coating and, therefore, corrosion can progress underneath the epoxy coating, while the coating itself remains unaffected.
b. Prolonged exposure to sunlight can be a cause of unacceptable degradation of the epoxy coating due to the ultra violet radiation from the sunlight. Such a problem is only likely to be more acute in a tropical country like India.
In view of the above it can be concluded that the real root of all controversy is that under some PERFECT conditions it may be possible to demonstrate some outstanding performance for Fusion Bonded Epoxy Coated Bars. However, under realistic situations Fusion Bonded Epoxy Coated Bars are not only suspect but also have known to lead to serious premature 恶化的关键结构。
I hope this will help in putting some of your doubts to rest.
********************************DISCLAIMER*********************************** Information contained and transmitted by this e-mail is confidential and proprietary to Tata Steel Ltd. and is intended for use only by the addressee. If you are not the intended recipient , you are notified that any dissemination or copying of this e-mail is strictly prohibited and you are requested to delete this e-mail immediately and notify the originator. Tata Steel does not enter into any binding agreement with any party by e-mail. Any views expressed by an individual do not necessarily reflect the view of Tata Steel. Tata Steel is not responsible for the consequences of any actions taken on the basis of information provided. While this e-mail has been checked for all known viruses the addressee should also scan for viruses. To know more about Tata Steel please visitwww.tatasteel.com ********************************************************************************