Dear Mr. Tom Joe You have raised a very important question: QUOTE "With FBEC ruled out as a effective method, there in an urgent need to identify some superior coating protection to steel. Please suggest some options which can be used and provides cathodic protection and good abrasion resistance." UNQUOTE On Studying Various options I have come to a conclusion that Galvanized Rebars is the best bet considering the effectiveness, cost and reliability aspects. In the paragraphs below I provide some arguments to support my viewpoint.
A barrier coating must satisfy the following conditions in order to be effective for its stated purpose of application on reinforcement bars.
1. It must form strong bond with steel which is not easy to peel off. 2. It must not impair bonding of the rebars with concrete. 3. It must withstand normal abrasion and impact in handling storage and application. 4. It must offer effective resistance to chloride attack 5. It must allow Bending and manipulation of bars without peeling
With this backdrop we may proceed to examinegalvanising as a suitable option.
reinforcement bars, In a tropical country like ours, where the moisture levels are high for most part of the year and the reinforcement bars have a relatively long travelling and waiting time before they are actually embedded in concrete, a galvanized coating is particularly useful to prevent early rusting of the steel. GALVANIZING PROVIDES VISIBLE ASSURANCE THAT THE STEEL HAS NOT RUSTED TILL AT THE POINT OF BEING EMBEDDED INTO CONCRETE.
Zinc coating serves its intended purpose of protection against corrosion in two distinct and significant ways of action - THE BARRIER ACTION AND THE SACRIFICIAL ACTION 1)Barrier action: Galvanizing provides a tough METALLURGICALLY BONDED zinc layer that completely covers the steel surface and acts as a barrier coating, which effectively prevents the access of any aggressive corrosive ionic species to the steel surface. The common method for galvanizing reinforcement bars is hot dip galvanizing, in which the bars are immersed in a bath of molten zinc, maintained at a temperature of around 450 Deg. C. The thickness of the zinc coating increases with the duration of immersion as well as the temperature of the bath. SINCE, THE BARS ARE COMPLETELY DIPPED IN A LIQUID BATH (OF ZINC) ALL PARTS OF THE BARS ACQUIRE THE COATING ALMOST UNIFORMLY. The coating is metallurgically bonded to the surface of steel. There is a soft outer layer of almost pure zinc (Hardness 70 VPN), 这造成to the toughness and impact resistance of the coating. Deeper inside there is a continuous series of zinc iron alloy layersas shown below:
ZETA 94% Zn - 180 VPN DELTA 90% Zn - 245 VPN GAMA 75% Zn - 250 VPN
These layers are metallurgically bonded to each other and ultimately to the base steel. THESE ALLOY LAYERS ARE FAR HARDER THAN ORDINARY ZINC, thereby offering appreciable abrasion resistance to the coating during handling. This strong metallurgical bond also ensures that NO UNDER-FILM CORROSION CAN OCCUR in a galvanized bar. Zinc has an amphoteric nature and has the ability to passivate due to the formation of protective reaction product films in the concrete environment. Reaction of zinc with fresh cement leads to passivity by formation of a diffusion barrier layer of zinc corrosion products. GALVANIZED REINFORCEMENT STEEL CAN WITHSTAND EXPOSURE TO CHLORIDE ION CONCENTRATION SEVERAL TIMES HIGHER THAN WHAT CAUSES SEVERE CORROSION IN BLACK STEEL BARS. While black steel in concrete typically de-passivate below a pH of 11.5, GALVANIZED REINFORCEMENT CAN REMAIN PASSIVATED AT A FAR LOWER pH - EVEN AS LOW AS 6.0. This largely negates the effect of the eventual progress of carbonation. These two factors combined i.e. the chloride tolerance and the resistance to carbonation makes galvanized coating a particularly effective one in protecting steel embedded in concrete. 2. Sacrificial action: Zinc occupies a position higher than iron in the galvanic series. Therefore, zinc will have a greater tendency to lose electron compared to steel. As a result, when zinc and steel are in contact in the presence of an electrolyte, zinc is slowly consumed by anodic dissolution, while steel is protected as a cathode. THE SACRIFICIAL ACTION OF ZINC IS MOST SIGNIFICANT IN SMALL DISCONTINUITIES SUCH AS COATING DEFECTS AND CUT EDGES. The total life of galvanized coating in concrete is the sum of the time it takes for zinc to depassivate (which itself is longer than the time taken by bare steel) - the barrier effect, PLUS the time it takes for the dissolution of the alloy layers in the zinc coating - the sacrificial effect. Substantial corrosion of steel can commence only after the zinc layer has been dissolved out of an appreciable area of steel surface. The result of this combined effect has been verified by salt spray test for 19 days. Bare steel was completely and severely corroded within a few days while only specs of white rust appeared on the galvanized rebars.
CORROSION PRODUCTS OF ZINC OCCUPY A SMALLER VOLUME than the corrosion products of ion. Therefore, these contribute little towards build up of internal stresses in the concrete during the initial process of corrosion. The corrosion products of zinc are also capable of migrating from the surface of the reinforcement into the concrete matrix, thus considerably reducing the likelihood of zinc corrosion induced spalling of concrete.
Galvanized bars are particularly convenient for storage and handling which is especially relevant for a large country like ours with fairly adverse climatic conditions in general. The bars may be stored outdoors (there is 不需要为我提供了掩盖这些酒吧)ths without rusting. Under similar conditions a black bar would rust quite severely. These bars can be handled and placed in the concrete in the same manner as applicable for non-galvanized rolled bars with no special precaution or surveillance called for.
Zinc coating has a soft pliable outer layer, which is strongly and metallurgically bonded to the steel substrate. As such it is easy to bend these bars without appreciable peeling and rupture of the coating. Even if some cracks appear the sacrificial protection provided by zinc ensures that these do not form favorable sites for initiation of corrosion.
Since zinc reacts to the wet concrete mix it leads to formation of a strong bond with concrete. The bond strength of galvanized bars to concrete has been studied by University of California. Tests were done on concrete beams with plain or; deformed bars cast inverted in the top of the beam. Galvanized rebars showed equal or better bond strength than ungalvanized rebars in all conditions in both plain and, deformed types.
Galvanized reinforcement is quite commonly used in the Australia, New Zealand, Canada, USA, Korea, Taiwan and several other countries and has been found to be cost effective. A number of important structures have been constructed such as Flatts Bridge - Bermuda, Royal Bermuda Yacht Club, Long Dick Creek - IOWA, Key West - Florida, Seven Mile Bridge - Florida, New Cairns Opns. Base - Queensland, Housing & Urban Development Building - Washington D.C., Sydney Opera House, Parliament House - Canberra, Royal Yacht Club - Victoria, Breakwater Marina - Townsville, Penno's Wharf - St. George, Hamilton Dock, Parliament House - New Zealand, US Coast Guard Barracks, Crocker Building - San Francisco to name a few. A study was recently conducted to verify the effectiveness of galvanized rebars in use for years in various marine installations in Bermuda. The results demonstrate that over 95% of zinc remains unaffected even after prolonged exposure to very high chloride concentration. The steel, obviously can start corroding only when all the zinc is consumed.
Even in India, a number of structures have been constructed using galvanized rebars. A few of these are listed below along with the quantity of galvanized rebars used:
Lotus Temple, New Delhi - 300T Residential Building, JNPT, Uran - 1000T All India Institute of Physical Medical & Research, Haji Ali - 50T Residential Building, Wadala - 50T Mahanagar Gas Ltd, Mumbai - 50T Guest House, Mangalore - 50T Central Railway, Wadi Bunder - 450T Shree Anand Sukhram Trust, Malad - 250T
Based on these experiences in the country and abroad, it can be assumed that in near future galvanized bars will gain much more widespread popularity as elsewhere in the world.
Galvanized rebars are adequately covered by both Indian and international standards. In India the bars must satisfy IS: 12594, which stipulates coating thickens of 610 g/M Sq. for Class B coating and 915 g/M Sq. for Class A coating. Almost similar levels are stipulated also in ASTM A 767. It can be seen that an extremely heavy coating is prescribed keeping in view the long service life expected from the intended application. The other Indian standards related to galvanzed rebars are listed below:
IS 1786 : Specification for high strength deformed steel bars and wires for concrete reinforcement IS 2629 : Recommended practice for hot dip galvanizing of iron and steel IS 6745 : Methods for determination of mass of zinc coating on zinc coated iron and steel articles However A word of Caution must be mentioned here. The specifications call for a very high coating thickness. A bar unscrupulously or inadvertently coated to a much lower thickness is almost impossible for a user to spot. Maintenance of uniformity of coating also calls for good process control. As such, care needs to be exercised to ensure that the source supplying the galvanized rebars has a robust quality system and is prepared to certify the coating thickness. Unlike the case for galvanized roofing sheets replacement of a substandard and underperforming galvanized rebars on detection at a later date is practically impossible. Utmost care must therefore be taken in selection of a proven and dependable source of supply.
The facts presented here is based on work done at TATA STEEL and the information gathered from the following resources:
1. A Guide to specifying and inspecting hot dip galvanized reinforcing steel - "American Galvanizers Association", Colorado
2. ACI Committee 222, "Corrosion of Metals in Concrete", American Concrete Institute, 222R-85, 1985.
3. Adnrade, C et al. "Corrosion Behavior of Galvanized Steel in Concrete," 2nd International Conference on Deterioration and Repair of Reinforced 在阿拉伯海湾混凝土;程序1卷,pp. 395-410, 1987.
4. Arup, H. "The Mechanisms of the Protection of Steel by Concrete," 化工Reinfor会议的社会cement in Concrete Construction; London, June 1983.
5. Bird, C.E. "Bond of Galvanized Steel Reinforcement in Concrete;" Nature, Vol. 94, No. 4380, 1962.
6. Cornet, I. & Breseler, B. "Corrosion of Steel and Galvanized Steel in Concrete;" Materials Protection, Vol. 5, No. 4, pp. 69-72, 1966.
7. Hosfoy, A.E. & Gukild, I. "Bond Studies of Hot Dipped Galvanized Reinforcement in Concrete;" ACI, Journal, March pp. 174-184, 1969.
8. MacGregor, B.R. "Galvanized Solution to Rebar Corrosion;" Civil Engineering, UK, 1987.
9. Roberts, A.W. "Bond Characteristics of Concrete Reinforcing Tendons Coated with Zinc;", ILZRO Project ZE-222, 1977
********************************DISCLAIMER*********************************** Information contained and transmitted by this e-mail is confidential and proprietary to Tata Steel Ltd. and is intended for use only by the addressee. If you are not the intended recipient , you are notified that any dissemination or copying of this e-mail is strictly prohibited and you are requested to delete this e-mail immediately and notify the originator. Tata Steel does not enter into any binding agreement with any party by e-mail. Any views expressed by an individual do not necessarily reflect the view of Tata Steel. Tata Steel is not responsible for the consequences of any actions taken on the basis of information provided. While this e-mail has been checked for all known viruses the addressee should also scan for viruses. To know more about Tata Steel please visitwww.tatasteel.com ********************************************************************************