www.www.buonovino.com

STRUCTURAL ENGINEERING FORUM OF INDIA [SEFI]

Forum SubscriptionsSubscriptionsDigestDigest PreferencesFAQFAQSearchSearchMemberlistMemberlistUsergroupsUsergroupsRegisterRegisterFAQSecurity TipsFAQDonate
ProfileProfileLog in to check your private messagesLog in to check your private messagesLog in to websiteLog in to websiteLog in to websiteLog in to forum
Warning: Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.

Time period-Tall Building Design
Goto pagePrevious1,2
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies.Thank Post www.www.buonovino.com Forum Index->E-Conference on Tall Buildings
查看之前的话题::View next topic
Author Message
btgprasad
...
...


Joined: 05 Aug 2008
Posts: 125

PostPosted: Tue Nov 27, 2012 7:11 amPost subject: Reply with quote

Nicely explained krishnan Sir
!

tall structure have to maintain enough stiffness to be in allowable lateral drift limits both in wind and Earthquake loads hence that required stiffness control time periods.

however,If we see Tall chimneys (275m) time periods will be 4 sec.Earthquake forces seldom governs.
"In the most critical earthquake zone with zone factor of 0.36 and response reduction factor of 1.5, the earthquake response is almost matching with that of wind response but never been crossing the wind response." extracted from conclusion of a paper.


larger Time period cause so many problems like Flapping,wind resonance for which mathematical idealization would be difficult and requires wind tunnel to analyze.here there is not concept of max limit of time period ,its concept of response.

I this context I want ask is there any process to take care of tolerances (error) in time period form actual field value.


Btg

Do you know .maximum drift allowed in Burj ?
it more than half a meter.
Back to top
View user's profileSend private message
sarfaraj.husain
...
...


Joined: 26 Jan 2003
Posts: 90

PostPosted: Tue Nov 27, 2012 7:21 amPost subject: Time period-Tall Building Design Reply with quote

in continuation to my trailing mail..........

for h >300m "T" goes on increasing..... (in general)

..........how to caliberate such flexibility with " Sa/g" for analysis & design.....


sarfraj




dear all

consider a tall building of height h =300m

time pd. T =0.075*300^0.75 =5.4 secs

how to get Sa/g ..........as per 1893-2002 all formula valid for T<= 4.00 secs...

if it is correct ...please clear my doubt...

sarfraj


-- ��

Posted via Email
Back to top
View user's profileSend private message
gautam chattopadhyay
...
...


Joined: 17 Feb 2009
Posts: 129

PostPosted: Wed Nov 28, 2012 2:41 amPost subject: Time period-Tall Building Design Reply with quote

Sarfraz, first of all the formula you are using in computing fundamental time period is very empirical. A building 300 m high must have 75 to 100 floors suggesting as many lumped masses as the number of floors and number of springs = number of floors. Hence the dynamic stiffness matrix and the mass matrix will be of order 75 x 75 to 100 x 100. Since natural frequency is the eigen value of the dynamic matrix ([K]/[M]), 75 to 100 eigen values will appear off the characteristic equation of the dynamic matrix. I feel now you can follow that predicting natural frequency and hence the time period is not an easy task. Time period is given by 2*(pie)/n where n is natural frequency (eigen value) computed from above. I feel it is dangerous to impose such empirical formula on tall buldings which should be analysed as a MDOF system as I described above.

On Tue, Nov 27, 2012 at 4:39 PM, sarfaraj.husain forum@www.buonovino.com)> wrote:
Quote:
dear all

consider a tall building of height h =300m

time pd. T =0.075*300^0.75 =5.4 secs

how to get Sa/g ..........as per 1893-2002 all formula valid for T<= 4.00 secs...

if it is correct ...please clear my doubt...

sarfraj


-- ��








Posted via Email
Back to top
View user's profileSend private message
sarfaraj.husain
...
...


Joined: 26 Jan 2003
Posts: 90

PostPosted: Wed Nov 28, 2012 4:46 amPost subject: Time period-Tall Building Design Reply with quote

Mr. Gautam

i 100% agree with your post that "T" is a function of mass & stiffness........and it can be carried out only by any software like staad etc ...( for > 3x3)......

the term eigen value,stiffness, MDOF are related to structural dynamics & are correct way to get "T".....

但是T = 0.075 h ^ 0.75刚度(独立)说our1893......point is how can we follow this for tall structures.......refer clause 7.8.2 to scale up the responses as against T ( T = 0.075h^0.75 as per 7.6)....
is there any convergence for this......


sarfraj...



From: "gautam chattopadhyay"
To:econf34289@www.buonovino.com,
Date: 11/28/12 08:44 AM
Subject: [E-CONF] Re: Time period-Tall Building Design



Sarfraz, first of all the formula you are using in computing fundamental time period is very empirical. A building 300 m high must have 75 to 100 floors suggesting as many lumped masses as the number of floors and number of springs = number of floors. Hence the dynamic stiffness matrix and the mass matrix will be of order 75 x 75 to 100 x 100. Since natural frequency is the eigen value of the dynamic matrix ([K]/[M]), 75 to 100 eigen values will appear off the characteristic equation of the dynamic matrix. I feel now you can follow that predicting natural frequency and hence the time period is not an easy task. Time period is given by 2*(pie)/n where n is natural frequency (eigen value) computed from above. I feel it is dangerous to impose such empirical formula on tall buldings which should be analysed as a MDOF system as I described above.

On Tue, Nov 27, 2012 at 4:39 PM, sarfaraj.husainforum@www.buonovino.com)> wrote:--auto removed--

Posted via Email
Back to top
View user's profileSend private message
KABIRDASGUPTA
SEFI Member
SEFI Member


Joined: 24 Aug 2010
Posts: 2

PostPosted: Wed Nov 28, 2012 5:26 amPost subject: Time period-Tall Building Design Reply with quote

Subject: [E-CONF] Re: Time period-Tall Building Design
From:forum@www.buonovino.com
Date: Tue, 27 Nov 2012 16:39:05 +0530
To:econf34289@www.buonovino.com

dear all

consider a tall building of height h =300m

time pd. T =0.075*300^0.75 =5.4 secs

how to get Sa/g ..........as per 1893-2002 all formula valid for T<= 4.00 secs...

if it is correct ...please clear my doubt...

sarfraj



Dear Mr Sarfraj,

All Values of Sa/g are same for T more than 4.0 sec.

Regards,

KABIR DASGUPTA

-- ��

Posted via Email
Back to top
View user's profileSend private message
swamikrishnan
E-Conference Moderator


Joined: 28 Jul 2011
Posts: 18

PostPosted: Wed Nov 28, 2012 11:30 pmPost subject: Re: Time period-Tall Building Design Reply with quote

To add to my earlier comment on long period ground motions, the response spectra for the Central Business District of Christchurch in the Feb 22, 2011, Christchurch earthquake are given in the following document:

http://www.ipenz.org.nz/christchurch-spectra.pdf

Note the conspicuous bump in the spectra between periods 2.75s and 3.75s; compare this against the NZS1170 design spectrum. The observed spectral acceleration at 3.25s period is about four times the design spectral acceleration for a 500-year event (Figure 3) and about twice the design spectral acceleration for a 2500-yr event (Figure 2).

显然,观察频谱不展览the smooth 1/T drop in the design spectrum. Similar long-period "bumps" can be seen in response spectra of near-source records such as the Rinaldi and Sylmar records observed in the 1994 Northridge earthquake.

Swaminathan Krishnan
California Institute of Technology

krishnan at its.caltec... wrote:

(ii) Dynamics: The more flexible longer period structures are more
susceptible to long-period long-duration ground motion. Such ground
motion is produced by large magnitude earthquakes (moderate
earthquakes can also produce long-period pulse-like ground motion in
the near-source region) and get amplified in deep sedimentary basins
and/or soft soil deposits. Unfortunately, there are not enough number
of records from such earthquakes collected in basins around the world.
As a result, the global dataset on which all design spectra are based
upon is deficient in long-period motion. Ground motion from
relatively small magnitudes tend to have much less long-period content
and the 1/T dropoff is reasonable for such conditions. The demands in
the longer-period regime from these rare large events may be much
greater than what the code spectra across the globe seem to suggest.
The 1985 Mexico city earthquake demonstrated this; more recently, the
Christchurch event reinforced this (although this was not a large
event, the longer period ground motions were greatly amplified by the
soft soils).As engineers we must decide, whether to protect our
structures against such rare events or bet against the occurrence of
such events during the lifetime of the building.



Posted via Email[/quote]
Back to top
View user's profileSend private messageVisit poster's website
Manoharbs_eq
General Sponsor
General Sponsor


Joined: 17 Jul 2012
Posts: 423

PostPosted: Thu Nov 29, 2012 4:21 amPost subject: Reply with quote

Higher the time period lower the frequency, hence low frequency structures attract lesser seismic forces. beyond time period 4 there is no significant change in acceleration value, critical is low frequency structures whose time period is less than 0.6 or so.

we can follow the value for 4 for more than 4 since further there is no significant change.

however how is that structure of 300m high is bare frame?.

if the structure is with infill we can use 0.9h/sqrtd.


Rgds
Manohar
Back to top
View user's profileSend private message
Display posts from previous:
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies.Thank Post www.www.buonovino.com Forum Index->E-Conference on Tall Buildings All times are GMT
Goto pagePrevious1,2
Page2of2



Jump to:
Youcannotpost new topics in this forum
Youcannotreply to topics in this forum
Youcannotedit your posts in this forum
Youcannotdelete your posts in this forum
Youcannotvote in polls in this forum
Youcannotattach files in this forum
Youcandownload files in this forum


© 2003, 2008 SEFINDIA,Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service.advertisement policy
Baidu
map