Dear All,
As per clause 27.2 of IS-456:2000, the structures exceeding 45 mtr in length are to be designed with one or more expansion joints.�
Considering that below ground the effect of temperature is less, one should provide joints in basement portions at a spacing of about 90.0 mtr.� When joints are provided more than 90 mtr spacing, cracks do appear after passage of time due to creep effect even if we provide shrinkage strips during casting.
Whenever building dimensions exceeds 45 mtr one should do temperature and shrinkage analysis by adding one more primary load case.� The load factors to be considered while combining temperature, shrinkage load with DL and LL are as under as per SP:24:983
� 1. ��1.4 �(D.L.+T) � 2. � �0.75 (1.4 DL+1.4 T + 1.7 LL)
Note:��� Earthquake separation joints between adjacent units shall be catered for as per clause 7.11.3 of IS 1893 (Part-I) 2002.
� � Regards, S C Mehrotra
Posted via Email |
|
Back to top |
|
 |
thirumalaichettiar Silver Sponsor


Joined: 26 Jan 2003 Posts: 3552
|
Posted: Sat Dec 01, 2012 3:51 pmPost subject: |
 |
|
Reference to Er.S C Mehrotra , I would like to bring another aspect of joint SEISMIC JOINT. This is different from Expansion joint. Viewers can browse the link below for some more informations onExpansion joint.
//www.buonovino.com/forum/viewtopic.php?t=9857
//www.buonovino.com/forum/viewtopic.php?t=5279
DILATION JOINT:
Browse the link below.
//www.buonovino.com/forum/viewtopic.php?t=6671
Seismic and Expansion joint
//www.buonovino.com/forum/viewtopic.php?t=5190
T.RangaRajan. |
|
Back to top |
|
 |
Surendra S SEFI Member

Joined: 25 Sep 2009 Posts: 16
|
Posted: Sat Dec 01, 2012 4:15 pmPost subject: Expansion Joints |
 |
|
Dear Sefians
Whether the clause 7.11.3 is practically possible in high rise buildings.? pls suggest...
rgds Surendra
On Sat, Dec 1, 2012 at 8:25 PM, subhash_mehrotra forum@www.buonovino.com)> wrote:
Quote: |
Dear All,
As per clause 27.2 of IS-456:2000, the structures exceeding 45 mtr in length are to be designed with one or more expansion joints.�
Considering that below ground the effect of temperature is less, one should provide joints in basement portions at a spacing of about 90.0 mtr.� When joints are provided more than 90 mtr spacing, cracks do appear after passage of time due to creep effect even if we provide shrinkage strips during casting.
Whenever building dimensions exceeds 45 mtr one should do temperature and shrinkage analysis by adding one more primary load case.� The load factors to be considered while combining temperature, shrinkage load with DL and LL are as under as per SP:24:983
� 1. ��1.4 �(D.L.+ T) � 2. � �0.75 (1.4 DL + 1.4 T + 1.7 LL)
Note:��� Earthquake separation joints between adjacent units shall be catered for as per clause 7.11.3 of IS 1893 (Part-I) 2002.
� � Regards, S C Mehrotra
|
Posted via Email |
|
Back to top |
|
 |
thirumalaichettiar Silver Sponsor


Joined: 26 Jan 2003 Posts: 3552
|
Posted: Sat Dec 01, 2012 4:56 pmPost subject: |
 |
|
Er.Surendra , Pl.inform which code the clause the clause 7.11.3 is present?
T.RangaRajan. |
|
Back to top |
|
 |
shahnawaz.sdk SEFI Member

Joined: 24 Jan 2010 Posts: 2 Location: Thane
|
Posted: Sun Dec 02, 2012 3:04 pmPost subject: Expansion Joints |
 |
|
Hi
Is there any book which can explain the calculation and effect of temperature n creep on buildings.
Regards
Shahnawaz Siddiqui Integrated Buildings
On 01-Dec-2012, at 20:25, "subhash_mehrotra" forum@www.buonovino.com)> wrote:
Quote: |
Dear All,
As per clause 27.2 of IS-456:2000, the structures exceeding 45 mtr in length are to be designed with one or more expansion joints.
Considering that below ground the effect of temperature is less, one should provide joints in basement portions at a spacing of about 90.0 mtr. When joints are provided more than 90 mtr spacing, cracks do appear after passage of time due to creep effect even if we provide shrinkage strips during casting.
Whenever building dimensions exceeds 45 mtr one should do temperature and shrinkage analysis by adding one more primary load case. The load factors to be considered while combining temperature, shrinkage load with DL and LL are as under as per SP:24:983
1. 1.4 (D.L.+ T) 2. 0.75 (1.4 DL + 1.4 T + 1.7 LL)
Note: Earthquake separation joints between adjacent units shall be catered for as per clause 7.11.3 of IS 1893 (Part-I) 2002.
Regards, S C Mehrotra
|
Posted via Email |
|
Back to top |
|
 |
Prasad Ghodekar SEFI Member

Joined: 04 Nov 2008 Posts: 1 Location: India
|
Posted: Sun Dec 02, 2012 6:43 pmPost subject: Expansion Joints |
 |
|
Hello Sir,
I am working on one of such kind of project. Do you have further study material for the same. Also, if you any example on this, please let me know.
Many Thanks.
Regards, Prasad Ghodekar.
On 1 December 2012 20:25, subhash_mehrotra forum@www.buonovino.com)> wrote:
Quote: |
Dear All,
As per clause 27.2 of IS-456:2000, the structures exceeding 45 mtr in length are to be designed with one or more expansion joints.�
Considering that below ground the effect of temperature is less, one should provide joints in basement portions at a spacing of about 90.0 mtr.� When joints are provided more than 90 mtr spacing, cracks do appear after passage of time due to creep effect even if we provide shrinkage strips during casting.
Whenever building dimensions exceeds 45 mtr one should do temperature and shrinkage analysis by adding one more primary load case.� The load factors to be considered while combining temperature, shrinkage load with DL and LL are as under as per SP:24:983
� 1. ��1.4 �(D.L.+ T) � 2. � �0.75 (1.4 DL + 1.4 T + 1.7 LL)
Note:��� Earthquake separation joints between adjacent units shall be catered for as per clause 7.11.3 of IS 1893 (Part-I) 2002.
� � Regards, S C Mehrotra
|
Posted via Email |
|
Back to top |
|
 |
sudeepmgs SEFI Member

Joined: 24 Sep 2009 Posts: 2
|
Posted: Mon Dec 03, 2012 5:15 amPost subject: Expansion Joints |
 |
|
Respected sir,
�� Thank you sir, this is very good information for row and high rise structures.
Regards,
SUDEEP MG Bangalore.
On Sat, Dec 1, 2012 at 8:25 PM, subhash_mehrotra forum@www.buonovino.com)> wrote:
Quote: |
Dear All,
As per clause 27.2 of IS-456:2000, the structures exceeding 45 mtr in length are to be designed with one or more expansion joints.�
Considering that below ground the effect of temperature is less, one should provide joints in basement portions at a spacing of about 90.0 mtr.� When joints are provided more than 90 mtr spacing, cracks do appear after passage of time due to creep effect even if we provide shrinkage strips during casting.
Whenever building dimensions exceeds 45 mtr one should do temperature and shrinkage analysis by adding one more primary load case.� The load factors to be considered while combining temperature, shrinkage load with DL and LL are as under as per SP:24:983
� 1. ��1.4 �(D.L.+ T) � 2. � �0.75 (1.4 DL + 1.4 T + 1.7 LL)
Note:��� Earthquake separation joints between adjacent units shall be catered for as per clause 7.11.3 of IS 1893 (Part-I) 2002.
� � Regards, S C Mehrotra
|