Posted: Mon Dec 11, 2006 4:49 pmPost subject: problem in placing of column & footing |
|
|
hi, Iam designing a G+3 floor building.Iam facing a problem in placing of column & footing.Here the borewell position is fixed and it is at a distance of 1feet 3 inches away fom column face. Now the architect is asking to place the footing such that it covers the borewell from all sides.There is no chance to make footing eccentric. Architect argument is that once the footing is cast there are no chances of removal of casing pipe and it does not affect the location.
Can u suggest is this possible.
Find out what India is talking about on - Yahoo! Answers India Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it NOW
Posted via Email |
|
Back to top |
|
|
dnnagaraj SEFI Member
Joined: 26 Jan 2003 Posts: 16 Location: Borivli(W)-Mumbai-400092
|
Posted: Mon Dec 11, 2006 7:02 pmPost subject: problem in placing of column & footing |
|
|
Dearkasturi1976@yahoo.co.in, Please fill the borewell with compacted sand and go ahead with normal procedure. The Architect, as well as the Structural aspects, are both satisfied. Regards, DNN
kasturi1976[AT]yah... wrote: hi, Iam designing a G+3 floor building.Iam facing a problem in placing of column & footing.Here the borewell position is fixed and it is at a distance of 1feet 3 inches away fom column face. Now the architect is asking to place the footing such that it covers the borewell from all sides.There is no chance to make footing eccentric. Architect argument is that once the footing is cast there are no chances of removal of casing pipe and it does not affect the location.
Can u suggest is this possible.
Find out what India is talking about on - Yahoo! Answers India Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it NOW
每个人都是疯狂的全新的Yahoo !邮件beta.
Posted via Email |
|
Back to top |
|
|
skatheassociates SEFI Member
Joined: 26 Jan 2003 Posts: 7
|
Posted: Thu Dec 14, 2006 10:01 amPost subject: problem in placing of column & footing |
|
|
Hello, You can place that colum/footing 1.2m or 1.5m away from borewell.i.e distance between colum face & borewell is equal to (1.2 m+1 ' 3") .(if that particular column is at outer face of Building) Take the cantilever bracket design from that colum to obstruct the borewell. Thanks & Regards Mr. Santosh Kathe
kasturi1976[AT]yah... wrote: hi, Iam designing a G+3 floor building.Iam facing a problem in placing of column & footing.Here the borewell position is fixed and it is at a distance of 1feet 3 inches away fom column face. Now the architect is asking to place the footing such that it covers the borewell from all sides.There is no chance to make footing eccentric. Architect argument is that once the footing is cast there are no chances of removal of casing pipe and it does not affect the location.
Can u suggest is this possible.
Find out what India is talking about on - Yahoo! Answers India Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it NOW
Find out what India is talking about on - Yahoo! Answers India Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it NOW
Posted via Email |
|
Back to top |
|
|
vikram.jeet General Sponsor
Joined: 26 Jan 2003 帖子:3699
|
Posted: Fri Dec 15, 2006 4:47 amPost subject: problem in placing of column & footing |
|
|
This will be quite risky as Bracket is one sided footing and it will create very high base pressure due to eccentricity and should be avoided.
It is better to fill the hole with sand and top 1.5 to 2.0m with mix 1:5:10 or leaner and go ahead with concentric footing.
with best wishes
vikramjeet
Posted via Email |
|
Back to top |
|
|
kasturi1976 SEFI Member
Joined: 26 Jan 2003 Posts: 6
|
Posted: Mon Dec 18, 2006 3:07 pmPost subject: problem in placing of column & footing |
|
|
Hi,
Can we place such a way that footing is concentric as usual and it covers the borewell area which is only of 6" diameter surrounded by casing pipe and footing reinforcement only is cut in that 6" dia region only.Any how column is 1feet 3inch away from borehole.
1) Does this gap of 1feet 3 inches between borehole and column centreline is ok? 2) Later stage if motor is inserted does this create any vibration in footing in working condition and affect the building structure?
Request to calrify. Kasturi
skatheassociates[AT]yah... wrote: Hello, You can place that colum/footing 1.2m or 1.5m away from borewell.i.e distance between colum face & borewell is equal to (1.2 m+1 ' 3") .(if that particular column is at outer face of Building) Take the cantilever bracket design from that colum to obstruct the borewell. Thanks & Regards Mr. Santosh Kathe
kasturi1976[AT]yah... wrote: hi, Iam designing a G+3 floor building.Iam facing a problem in placing of column & footing.Here the borewell position is fixed and it is at a distance of 1feet 3 inches away fom column face. Now the architect is asking to place the footing such that it covers the borewell from all sides.There is no chance to make footing eccentric. Architect argument is that once the footing is cast there are no chances of removal of casing pipe and it does not affect the location.
Can u suggest is this possible.
Find out what India is talking about on - Yahoo! Answers India Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it NOW
Find out what India is talking about on - Yahoo! Answers India Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it NOW
Send free SMS to your Friends on Mobile from your Yahoo! Messenger. Download Now!http://messenger.yahoo.com/download.php
Posted via Email |
|
Back to top |
|
|
|