�Dear sir/ madam , � �������������� ���It is good to have discussion session on IS :16700-2017 , the following are my queries, requesting �Draft team �and other members �to share views �/� give clarity .
1.������ �����Clause 1.6 of IS:16700� will state that “ in case of conflict , clauses given this standard shall be applicable “,� �the following are the conflict with IS 1893-2016
A.����� �Damping ratio of concrete as per� clause 6.2.24 of IS :16700 is 2% whereas it is 5% as per 7.2.4 of IS :1893, �is this reduction of damping ratio’s having any relations with building heights. � B.����� ��Lateral Drift ratio for factored load combinations limited to �H i/250 in �clause� 5.4� of IS :16700 �whereas �the same drift limits in Is :1893 clause7.11.1� is w.r.t service load combination with� factored �cracked section prosperities . Apart from that �this �drift ratios are not specified w.r.t� structural system in IS:16700� , shall we follow H/250 ��irrespective of structural system �if no �irregularities. �������������� 2.����Structural system �vs� Height limitations Can we get the clarifications for treating� the following systems as secondary /� low-grade or ��treating as �equal in lateral load resisting systems ����w.r.t� other �systems ��
a. Structural walls with moment frames �w.r.t� structural walls located at core b. Well distributed walls �w.r.t�� to Structural walls with perimeter systems c. Structural walls with Moment frames w.r.t� Structural walls with perimeter frames . is �perimeter frames indicates nominal frames or �deep beams.
with regards, prasad�����������