E-Conference on IS 16700 - Day 1 Discussions

This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies.Thank Post www.www.buonovino.com Forum Index->E-conference on IS 16700 13th March to 18th March 2018
View previous topic::View next topic
Author Message
Econf_Moderator
E-Conference Moderator


Joined: 26 Feb 2012
Posts: 23

PostPosted: Tue Mar 13, 2018 5:55 pmPost subject: E-Conference on IS 16700 - Day 1 Discussions Reply with quote

Dear All,


Thank you very much for the interesting discussions on the Day 1 of the E-conference on "IS 16700- Criteria for Structural Safety of Tall Concrete Buildings".


We would like to clarify some of the points raised during the discussion and would try to cover as many items are possible in our subsequent posts.


Comment: Deformation limit (Section 5.4): The section recommends the use of 50 year return period for the service wind drift limit. I feel this bit conservative. International codes generally considers 10 years return period for the service drift limitation.

Response: Noted and comment will be put up to Drafting group for discussion

Comment: �what is the Way forward,for the existing and under construction buildings� what about the thousands of Moment Frame Buildings, now not allowed in Zones IV and V at all?

Comment: As per Table 1 and Table 2, Moment Frame System is not applicable for buildings in seismic Zone IV and V. Basis for eliminating framing system altogether in high seismic zones is not made clear. This may require a review. As per fib bulletin-73, framing system is permitted in tall buildings upto a height of about 75m. This clause therefore should be reviewed.


回复:不需要申请项目的代码s under construction or for which the authority approvals are already obtained. Tall buildings of 50m and above are normally with lift core which can be used structurally to enhance the lateral stiffness of the building. The structural system then becomes Structural Wall + Moment Frame. It would be seldom possible to have tall buildings with only moment frames and would not be advisable to ignore the lift cores in the analysis.

Comment: 1.3 Is this a group pf buildings or a single building? Why is this applicable?

Response: Buildings with very high density need special features and enhanced building behaviour. This is a requirement in the aftermath of the collapse of World Trade Towers where it was understood that buildings with high density, regardless of how well they have been designed or constructed. have special requirements and need to be approached differently

Comment: Under floor system 5.6 sub clause 5.6.2.3 it is mentioned that "At any storey , the minimum width of floor slab along any section after deduction of openings shall not be less than 5 m and the minimum width of the slab beyond an opening to edge shall not be less than 2m".
Can anyone clarify the above clause also is it 5 sq m instead of 5 m.


Comment: 5.6.2.1 What is the criteria- unsupported length of the opening / slenderness limit/ axial force ? As we are using rigid diaphragm in most cases, this does not effect the analysis


Response: Diaphragm requirements are in line with those in international codes. Also refer to �Some Concepts in Earthquake Behaviour of Buildings�, Gujarat State Disaster Management Authority 2013http://www.iitk.ac.in/nicee/IITK-GSDMA/EBB_001_30May2013.pdffor a better understanding of effect of cutouts on diaphragm action.


Best Regards,


E-Conference Moderators
Back to top
View user's profileSend private message
hemalmistry
...
...


Joined: 01 Jul 2009
Posts: 70

PostPosted: Tue Mar 13, 2018 6:19 pmPost subject: Reply with quote

等待响应对查询关于最大体育rmissible concrete grade of M70
Back to top
View user's profileSend private message
abhio
...
...


Joined: 08 Mar 2010
Posts: 545

PostPosted: Wed Mar 14, 2018 4:58 amPost subject: Reply with quote

Dear Sir/ Madam,

Please also note the following:


CL 5.6.3. IN THIS IT IS STATED THAT " NATURAL VERTICAL
VIBRATION FREQUENCY OF ANY FLOOR SYSTEM SHALL NOT EXCEED 3 HZ
I believe this is an error in the Code. The 3 Hz limitation ought to be a lower bound, and not upper bound on the natural frequency of the floor.

Regards,

A S Oundhakar
Back to top
View user's profileSend private message
alpa_sheth
...
...


Joined: 26 Jan 2003
Posts: 278

PostPosted: Wed Mar 14, 2018 5:14 amPost subject: E-Conference on IS 16700 - Day 1 Discussions Reply with quote

I agree, this is a mistake and will be corrected in the eraata to be issued.�


Alpa�

On Wed, Mar 14, 2018 at 10:28 AM, abhio forum@www.buonovino.com)> wrote:
Quote:
Dear Sir/ Madam,

Please also note the following:


CL 5.6.3. IN THIS IT IS STATED THAT " NATURAL VERTICAL
VIBRATION FREQUENCY OF ANY FLOOR SYSTEM SHALL NOT EXCEED 3 HZ
I believe this is an error in the Code. The 3 Hz limitation ought to be a lower bound, and not upper bound on the natural frequency of the floor.

Regards,

A S Oundhakar







Posted via Email
Back to top
View user's profileSend private message
Display posts from previous:
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies.Thank Post www.www.buonovino.com Forum Index->E-conference on IS 16700 13th March to 18th March 2018 All times are GMT
Page1of1



Jump to:
Youcannotpost new topics in this forum
Youcannotreply to topics in this forum
Youcannotedit your posts in this forum
Youcannotdelete your posts in this forum
Youcannotvote in polls in this forum
Youcannotattach files in this forum
Youcannotdownload files in this forum


© 2003, 2008 SEFINDIA,Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service.advertisement policy
Baidu
map