Dear All,
We hope everyone had two good days of discussion on Sections 7 & 8. There were good level of participation and most of the queries and comments were discussed and responded by our fellow SEFIans.
One item which probably needs some clarification is:
Comment: Clause 7.3.11 is in contradiction with Table 1 in Section 5, which prohibits use of flat slab in Zone IV & V. But 7.3.11 says to ignore stiffness of flat slab.�Code should be consistent with its provisions, one can be confused to use whether use flat slab system or not in those zones.
Response: Clause 7.3.11 restricts the use of flat slab column frames stiffness to be considered for lateral resistance of the structure and Table 1 is consistent with this requirement by not listing it among acceptable lateral load resitting system. Flat slab could be used as gravity system subject the requirements of IS 1893.
Best regards,
E-Conference Moderators