Posted: Mon Mar 19, 2018 5:32 amPost subject: clause 7.2 Table 6 cracked section properties |
|
|
Dear Mr Krishna You are right and when we have multiple towers connected to a single podium, this needs to be done with an integrated model and for single towers/NTA separately, making it a scaring no of analyses. And then to check which one finally governs the design of a particular member. I wish the software guys become our saviours!!
Best Regards Sangeeta Wij President,WISE India Managing Partner SD Engineering Consultants LLP Vice President(North),Indian Association of Structural Engineers, Fellow and Chartered Engineer, Institution of Engineers H333 New Rajinder Nagar(Lower Ground Floor), New Delhi-110060 Ph:9811776210;01145128530
From:Gangisetty Krishna [mailto:forum@www.buonovino.com] Sent:15 March 2018 10:57 To:econf@www.buonovino.com Subject:[E-CONF] Re: clause 7.2 Table 6 cracked section properties
Alok sir,
In Table 6 of the code, it is specified that to do the crack section analysis for un-factored and factored load. What is the importance of the un-factored crack section analysis? when will be this analysis governs the section size and reinforcement in the design.
For the crack section is it required to do analysis 4 times with un-factored and factored properties with 2% damping for wind load, 5% damping for Earthquake load. The analysis becomes bit complex or not?
Thank you sir,
With regards,
G V Krishna