clause 7.2 Table 6 cracked section properties
Goto pagePrevious1,2
This forum is locked: you cannot post, reply to, or edit topics.这个话题被锁定:你不能edit posts or make replies.Thank Post www.www.buonovino.com Forum Index->E-conference on IS 16700 13th March to 18th March 2018
View previous topic::View next topic
Author Message
sangeeta_wij
...
...


Joined: 21 Apr 2016
Posts: 57

PostPosted: Mon Mar 19, 2018 5:32 amPost subject: clause 7.2 Table 6 cracked section properties Reply with quote

Dear Mr Krishna
You are right and when we have multiple towers connected to a single podium, this needs to be done with an integrated model and for single towers/NTA separately, making it a scaring no of analyses. And then to check which one finally governs the design of a particular member. I wish the software guys become our saviours!!



Best Regards
Sangeeta Wij
President,WISE India
Managing Partner
SD Engineering Consultants LLP
Vice President(North),Indian Association of Structural Engineers,
Fellow and Chartered Engineer, Institution of Engineers
H333 New Rajinder Nagar(Lower Ground Floor),
New Delhi-110060
Ph:9811776210;01145128530


From:Gangisetty Krishna [mailto:forum@www.buonovino.com]
Sent:15 March 2018 10:57
To:econf@www.buonovino.com
Subject:[E-CONF] Re: clause 7.2 Table 6 cracked section properties



Alok sir,

In Table 6 of the code, it is specified that to do the crack section analysis for un-factored and factored load. What is the importance of the un-factored crack section analysis? when will be this analysis governs the section size and reinforcement in the design.

For the crack section is it required to do analysis 4 times with un-factored and factored properties with 2% damping for wind load, 5% damping for Earthquake load. The analysis becomes bit complex or not?

Thank you sir,

With regards,

G V Krishna

Posted via Email
Back to top
View user's profileSend private message
Display posts from previous:
This forum is locked: you cannot post, reply to, or edit topics.这个话题被锁定:你不能edit posts or make replies.Thank Post www.www.buonovino.com Forum Index->E-conference on IS 16700 13th March to 18th March 2018 All times are GMT
Goto pagePrevious1,2
Page2of2



Jump to:
Youcannotpost new topics in this forum
Youcannotreply to topics in this forum
Youcannotedit your posts in this forum
Youcannotdelete your posts in this forum
Youcannotvote in polls in this forum
Youcannotattach files in this forum
Youcannotdownload files in this forum


© 2003, 2008 SEFINDIA,Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service.advertisement policy
Baidu
map