Posted: Wed Nov 12, 2014 4:19 pmPost subject: Why do we oly consider service loads while designing footing |
|
|
While designing footings we consider the service load combinations whereas while designing a beam or column we take factored load combinations ?? I am also confused about why we must consider service load combinations ( limit state of servicibility ex: 1.2D.L +0.9L.L) when we are applying bigger factors like 1.5D.L + 1.5L.L ( limit state of collapse ) ?? It is our choice between how safe and how economic design we want ?? |
|
Back to top |
|
|
stharish SEFI Member
Joined: 20 Aug 2010 Posts: 5
|
Posted: Sun Aug 09, 2015 1:24 amPost subject: Service loads used to determine bearing capacity |
|
|
Factored loads need to be considered for the design of footings, base plates, punching shears and for providing reinforcement.
Only for bearing stress you consider allowable loads. This is because...
Geotechnical engineer provides you allowable bearing capacity. In USA, a safety factor of 4 is provided for soil bearing stresses i.e. Ultimate bearing stress / allowable bearing stress = 4.
Regards, Harish
Last edited by stharish on Sun Aug 09, 2015 12:47 pm; edited 1 time in total |
|
Back to top |
|
|
B.V.Harsoda General Sponsor
Joined: 19 Jan 2009 Posts: 2329 Location: RAJKOT,GUJARAT, INDIA
|
Posted: Sun Aug 09, 2015 4:17 amPost subject: Re: Service loads used to determine bearing capacity |
|
|
Your explanation is correct, I agree with you. In India factor of safety 3 is taken to calculate the S.B.C. of soil.
stharish wrote: |
Factored loads need to be considered for the design of footings, base plates, punching shears, and providing reinforcement.
Only for bearing stress you consider allowable loads. This is because...
Geotechnical engineer provides you allowable bearing capacity. In USA, a safety factor of 4 is provided for soil bearing stresses i.e. Ultimate bearing stress / allowable bearing stress = 4.
Regards, Harish |
|
|
Back to top |
|
|
Zia SEFI Regulars
Joined: 28 May 2015 Posts: 33
|
Posted: Mon Aug 10, 2015 6:45 amPost subject: |
|
|
Hi Siddhartha,
You can also use limit stage design for the geotechnical design of footings.
In the strength limit state design, the geotechnical design strength taken as a geotechnical strength reduction factor times the ultimate geotechnical design strength shall be greater than the ultimate loads (i.e. design action effect). The geotechnical strength reduction factor depends on a number of factors and can range from 0.4 to 0.8.
Similarly in the serviceability limit state design, a suitable modulus reduction factor can be used in calculating settlements of footings for serviceability loads.
Regards, Zia |
|
Back to top |
|
|
es_jayakumar General Sponsor
Joined: 24 Nov 2011 Posts: 1408 Location: Cochin
|
Posted: Sun Oct 10, 2021 2:04 amPost subject: |
|
|
In continuation to the comments by Er.Zia, an article of me on the "Geotechnical Design of Foundations by LSD" published in the current CE&CR Magazine (excerpt attached) is expected to throw more light on this topic.
E S Jayakumar
Warning:
Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses. Use online scanners
here
and
here
to upload downloaded attachment to check for safety.
|
Description: |
|
Download |
Filename: |
Article.pdf |
Filesize: |
164.56 KB |
Downloaded: |
816 Time(s) |
|
|
Back to top |
|
|
维克ram.jeet General Sponsor
Joined: 26 Jan 2003 帖子:3699
|
Posted: Sun Oct 10, 2021 2:56 amPost subject: |
|
|
The FOS for bearing strata (soil/rock) is higher since : Testing is done at few locations , it is not done at each foundation location. Heterogeneous nature of soil /rocks Water table assessment is at time of testing In small projects SBC is either taken from nearby sites OR even assumed Pressure bulb beneath footing depends upon nature of bearing (strata type /rock )as also foundation system. But in design uniform pressure is taken under foundation ,for working out bearing area.
因此,我认为在terms of Limit stage , The load factor for foundation bearing area requirement is 3.0 or 2.5 as per soil. Whereas Load Factor for structure design of structural components is about half since heterogeneity and other factors are not imperative in structure work. |
|
Back to top |
|
|
|