Er Ramu
Calculations for deflection Chek purposes:
As per calcs fm u , pt = 0.128 for LF =1.0
Refer to chart figure 3 , the multiplier is 2.0
The effect of continuity cannot be taken twice , the % reinforcement worked is based on continuity and there fore Gross value of L/d = 2*20= 40
Hence eff depth = 327/40 = 8.2cm Overall depth = 8.2+ 2= 10.2 cm cf 11.5 ok - - - This is as per clause 22.2.1
Also as per clause 23.1 for slabs as already discussed , L/D = 32 Hence D , the o/all depth = 327/32 = 10.22 cm , just the same
Calculation for reinf provision : Actual reinf to be provided based on LF= 1.5 Hence Mu/bd^2 = 0.426*1.5 = 0.639 pt = 0.187 Ast 0.187*9.5= 1.78 cm2/m |
|
Back to top |
|
|
vikram.jeet General Sponsor
Joined: 26 Jan 2003 Posts: 3689
|
Posted: Mon Aug 08, 2022 3:10 pmPost subject: |
|
|
One thing must be borne in mind that while making deflection check using load factor = 1.0 , pl calculate pt and see modification factor and do not further calculate Ast , Since Ast to be provided has to be based on Pt using Load factor =1.5.
Just my view after seeing yr calcls |
|
Back to top |
|
|
vikram.jeet General Sponsor
Joined: 26 Jan 2003 Posts: 3689
|
Posted: Mon Aug 08, 2022 3:28 pmPost subject: |
|
|
Er Ramu
Cantilever slab
Your calcs are OK and depth rightly revised . Cantilever slabs must be provided with liberal depth as reinf is at top and chances of reinf getting little down at site are very much there inspite of placing chairs precautions . Even some designers always take view of this and provide some additional reinf at Cantilever slabs , though many designers who are very rigid may not encourage this . But while providing we have to judge site situations and should not act as theoretical tigers. |
|
Back to top |
|
|
ramu_se ...
Joined: 30 Oct 2017 Posts: 101
|
Posted: Mon Aug 08, 2022 4:22 pmPost subject: |
|
|
Thank you sir for giving such a brief explanation.
Why do we have to use the load factor as 1 for % of reinforcement calculation to find out the modification factor?
Is there any specfic codal provison for this?
To calculate fs we need to know Ast required and Ast provided, so this Ast is based on load factor 1 or load factor 1.5?
Thanks & Regards, Ramu. |
|
Back to top |
|
|
vikram.jeet General Sponsor
Joined: 26 Jan 2003 Posts: 3689
|
Posted: Tue Aug 09, 2022 3:24 amPost subject: |
|
|
Deflection is serviceability requirement and as per IS 456 this needs to be checked at working loads as evident from clause 35.4 on partial safety factors for Loads Table 12 ( relating clauses 18.3 and 35.4.1 of IS 456 1978).
The Load factor for serviceability limits is( 1.0 DL + 1.0 LL) |
|
Back to top |
|
|
spsvasan ...
Joined: 18 Dec 2008 Posts: 369
|
Posted: Sun Aug 14, 2022 10:11 amPost subject: |
|
|
Dear Er.Ramu & Er.Vikramjeet
I am generally in agreement with Er.Vikramjeet. However, I differ in one aspect only
fs = 0.58 x fy x Ast(required) / Ast(provided) fs = 0.58 x 415 x 122 / 250 = 117.46 N/mm2 As per Fig.4 in IS-456:2000 M.F = 2.0
在上面的计算,恕我直言,Ast(必需)是to be the limit state requirement only, ie 178 sqmm/m.
In the expression fs= 0.58 fy(As reqd / As provided), the factor 0.58 lowers the limit state stress to the service stage level
In this particular case, the modification factor still remains as 2.0
S.P.Srinivasan |
|
Back to top |
|
|
vikram.jeet General Sponsor
Joined: 26 Jan 2003 Posts: 3689
|
Posted: Mon Aug 15, 2022 3:27 pmPost subject: |
|
|
spsvasan wrote: |
Dear Er.Ramu & Er.Vikramjeet
I am generally in agreement with Er.Vikramjeet. However, I differ in one aspect only
fs = 0.58 x fy x Ast(required) / Ast(provided) fs = 0.58 x 415 x 122 / 250 = 117.46 N/mm2 As per Fig.4 in IS-456:2000 M.F = 2.0
在上面的计算,恕我直言,Ast(必需)是to be the limit state requirement only, ie 178 sqmm/m.
In the expression fs= 0.58 fy(As reqd / As provided), the factor 0.58 lowers the limit state stress to the service stage level
In this particular case, the modification factor still remains as 2.0
S.P.Srinivasan |
Yes , In case stress is calculated instead of reinf % pt at LF=1.0 , factor fs be based as rightly expressed by Er SP Srinivasan. |
|
Back to top |
|
|
BVRAO General Sponsor
Joined: 21 Sep 2009 Posts: 47
|
Posted: Tue Aug 16, 2022 1:03 pmPost subject: |
|
|
Slab Design with deflection check
Warning:
Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses. Use online scanners
here
and
here
to upload downloaded attachment to check for safety.
|
Description: |
Slab Design with deflection check |
|
Download |