what should be the minimum slanting angle for brickwork of circular manhole chamber

Post new topicReply to topicThank Post www.www.buonovino.com Forum Index->Speak Out Box
View previous topic::View next topic
Author Message
sspawar
...
...


Joined: 05 Jun 2009
Posts: 1199

PostPosted: Sat Oct 29, 2022 12:11 amPost subject: what should be the minimum slanting angle for brickwork of circular manhole chamber Reply with quote

Dear Sefians,
There many type of circular manhole chambers are in practice. But what should be the slanting angle of brickwork closing at mouth from larger diameter in lower side, when we are using M7.5 one brick wall with mortar 1:4 and plastering inside 1:3 12mm thick.
Image result for circular manhole chamberwhat should be the minimum slanting angle of circular frustum for brickwork of circular manhole chamber? how much top collar vertically can be erected safely above tip of circular frustum?

Regards
Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
帖子:3699

PostPosted: Sat Oct 29, 2022 4:20 amPost subject: Reply with quote

As per Book ' NABHI'S PRACTICAL HANDBOOK FOR BUILDING CONSTRUCTION ' by Er MKGupta ( Retd CPWD) an angle of 1 (H) : 5(V) is indicated at page 641 giving details of manhole.

Further from design point of view , It is better to have small dia circular bars reinforcement in masonry mortar at start of junction of taper & vertical masonry, at least in two courses mortar. Reinf can be two nos circular bars along masonry in two courses making total 4 nos . Bars must be closed with lap Length. This can take hoop force generated at junction even if passive resistance of soil insufficient.

Other way is to provide higher section of masonry at junction say 345x345 or 460x460 as ring beam to bear any net Tensile stresses in horizontal direction as result of hoop tension at junction.
Back to top
View user's profileSend private message
Display posts from previous:
Post new topicReply to topicThank Post www.www.buonovino.com Forum Index->Speak Out Box All times are GMT
Page1of1



Jump to:
Youcannotpost new topics in this forum
Youcannotreply to topics in this forum
Youcannotedit your posts in this forum
Youcannotdelete your posts in this forum
Youcannotvote in polls in this forum
Youcannotattach files in this forum
Youcandownload files in this forum


© 2003, 2008 SEFINDIA,Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service.advertisement policy
Baidu
map