dubeyratnesh SEFI Regulars
Joined: 21 Mar 2022 阿宝sts: 38
|
阿宝sted: Fri Apr 01, 2022 9:13 am阿宝st subject: pedestal design for light pole |
|
|
hello sir i want to design a pedestal with footing on soil having sbc 8 t/m2.pedestal is supporting 9m high light pole in an area having basic wind speed 50 m/s. what approach we can follow to design this pedestal and footing |
|
Back to top |
|
|
维克ram.jeet General Sponsor
Joined: 26 Jan 2003 阿宝sts: 3699
|
阿宝sted: Sat Apr 02, 2022 3:32 am阿宝st subject: |
|
|
Pedestal & footing for high mast
Wind load is predominant and substructure is designed for moment due to wind forces on high mast body.
Generally square pedestal and square shape footing for ease of reinf placement vis a vis circular one.
Footing size as also foundation depth shall be sufficient enough to provide soil weight over footing . Footing shall be checked for overturning . Sliding may not be a problem but to be checked .
Base pressures needs to be checked considering some upliftment of footing due to wind. e = M/W M is the moment at base due to wind forces W is the wt of footing + soil wt over it + wt of steel mast The contact length X = 3*(B/2 - e) B is the dimension of footing in direction of moment Contact Length percentage = (X/B)*100
Contact % can be 67% to 80% depending on FOS against OT
Max base pressure = 2*W /( X*L) L is the dim of footing in other direction
Some designers also consider passive soil resistance relief with some FOS provided by rcc pedestal and footing |
|
Back to top |
|
|
dubeyratnesh SEFI Regulars
Joined: 21 Mar 2022 阿宝sts: 38
|
阿宝sted: Sat Apr 02, 2022 3:38 am阿宝st subject: pedestal design for light pole |
|
|
SIR ON WHAT BASIC DEPTH OF PEDESTAL WILL BE CALCULATED OVER FOOTING. |
|
Back to top |
|
|
维克ram.jeet General Sponsor
Joined: 26 Jan 2003 阿宝sts: 3699
|
发布:2022年坐4月2日的专机阿宝st subject: |
|
|
Pedestal shall also be rcc in square crossection .
Pedestal is designed as vertical cantilever from footing .
Depth of foundation for 9.0m mast may be minimum 2.5 m . But all depend on soil weight needed over footing . If foundation size is restricted , then higher depth of foundation is needed to achieve soil weight. |
|
Back to top |
|
|
dubeyratnesh SEFI Regulars
Joined: 21 Mar 2022 阿宝sts: 38
|
阿宝sted: Sun Apr 03, 2022 11:36 am阿宝st subject: Design of pedestal for electric pole |
|
|
Thank you sir From where we can start ? On what basis we can select hight of pedestal.? Taking factor of safety about 1.5 for overturning the hight of pedestal is coming more than 4 meter which is not feasible.a 9 meter hight pole on cyclone effected area gives more wind moment? Weight of pedestal resisting will be more? How to decide pedestal hight.further footing design? |
|
Back to top |
|
|
维克ram.jeet General Sponsor
Joined: 26 Jan 2003 阿宝sts: 3699
|
阿宝sted: Sun Apr 03, 2022 3:45 pm阿宝st subject: |
|
|
You are thinking of block foundation for light pole . I think in this case Pl think of rcc spread footing with soil over it with rcc pedestal. The concrete block foundations are feasible for low ht light poles , but not for high mast which require spread footing with rcc pedestal. |
|
Back to top |
|
|
dubeyratnesh SEFI Regulars
Joined: 21 Mar 2022 阿宝sts: 38
|
阿宝sted: Mon Apr 04, 2022 3:06 am阿宝st subject: Design of pedestal for electric pole |
|
|
Sir can you provide any design example of high mast from any refrence book or previous design? |
|
Back to top |
|
|
维克ram.jeet General Sponsor
Joined: 26 Jan 2003 阿宝sts: 3699
|
阿宝sted: Mon Apr 04, 2022 4:05 am阿宝st subject: |
|
|
I don't think that any ready standard design / details available , but you can search NHAI or Highways / Expressways for any ready material.
But it is a simple case of designing an isolated spread footing for Uniaxial moment. Footing need to be square as wind can blow in any direction . |
|
Back to top |
|
|
维克ram.jeet General Sponsor
Joined: 26 Jan 2003 阿宝sts: 3699
|
阿宝sted: Mon Apr 04, 2022 4:39 am阿宝st subject: |
|
|
Pl see in google search details for standard street light pole upto 35 feet high Search P-660.pdf on Google.
Last edited by vikram.jeet on Mon Apr 04, 2022 5:40 am; edited 2 times in total |
|
Back to top |
|
|
维克ram.jeet General Sponsor
Joined: 26 Jan 2003 阿宝sts: 3699
|
阿宝sted: Mon Apr 04, 2022 5:03 am阿宝st subject: |
|
|
Please see in google search for light pole design calcs , are available in net |
|