ramu_se ...
Joined: 30 Oct 2017 Posts: 101
|
Posted: Fri Apr 13, 2018 10:22 amPost subject: Combined footing design in staad - load application |
|
|
Hi All,
Iam designing combined footing in staad using plate elements by assigning support conditions as elastic mat throughout the area of footing.
How to apply load on columns? Is is right if we apply loads of the respective column divided by area of footing as a plate pressure on the column? Please clarify me?
Thank you, Ramu. |
|
Back to top |
|
|
es_jayakumar General Sponsor
Joined: 24 Nov 2011 Posts: 1408 Location: Cochin
|
发布:2018年4月13日星期五下午16点Post subject: |
|
|
I think, your proposition is sensible. If we apply column loads as point loads, the analysis is likely to indicate unrealistic concentration of stresses / moments around the point loads. Please ensure that the plate size is so chosen that the column dimensions are multiples of the dimension of the plate, for compatibility in application of column load as UDL.
E S Jayakumar |
|
Back to top |
|
|
ramu_se ...
Joined: 30 Oct 2017 Posts: 101
|
Posted: Sun Apr 15, 2018 12:20 amPost subject: |
|
|
Thank you sir.
我申请了每个列的负载压力(load/Area) and i have attached the staad file for your reference.
Iam little confused to apply the column load as UDL.
Please clarify me which is the correct method to apply loads on column.
Thank you.
Ramu.
Warning:
Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses. Use online scanners
here
and
here
to upload downloaded attachment to check for safety.
|
Description: |
|
Download |
Filename: |
Combined footing_.zip |
Filesize: |
3.68 KB |
Downloaded: |
431 Time(s) |
|
|
Back to top |
|
|
es_jayakumar General Sponsor
Joined: 24 Nov 2011 Posts: 1408 Location: Cochin
|
Posted: Sun Apr 15, 2018 5:23 amPost subject: |
|
|
I find your column size is 0.70m x 0.20m. Suppose your column load is 1400kN. Then the Plate UDL you have to apply over an area of 0.70m x 0.20m is 1400/(0.70*0.20) = 10000 kN/m2. I think, there is some confusion in your comprehension.
E S Jayakumar |
|
Back to top |
|
|
ramu_se ...
Joined: 30 Oct 2017 Posts: 101
|
Posted: Mon Apr 16, 2018 9:49 amPost subject: |
|
|
Thank you sir,understood clearly.After this analysis, we have to design the footing for maximum Mx & My from plate contours,and check for one way and two way shear.Please clarify me.
Thank you Ramu. |
|
Back to top |
|
|
|